WCEI
- Central Virginia
- President/Owner, Wayne Cook Electric, Inc.
Situation: large fresh water lake, (17 miles long).
floating aluminum boat dock.
Boat dock was originally installed a couple of years ago with no power installed.
Customer had us install a few lights and 120 volt receptacles. Installation was installed to code and inspected.
Customer started reporting a tingling sensation when he was in the water and reached within a few inches of the aluminum ladder. Prior to installation of power, he had not noticed this sensation.
We entered the water and could feel the same sensation. Of course we disconnected all power to perform this test. But with the power on or off, we could feel the same sensation at the same intensity.
There are no other docks within close proximity of this customer’s dock.
However, the local power utility company has a set of high voltage transmission lines crossing this body of water approximately 400 yards away. ( I say this because a few miles away, a different power company has an even larger set of transmission lines that run adjacent to a major county sports complex. The parking lot is partially under these transmission lines and the steel parking lot light poles will give you a good jolt if you are grounded. Before anyone ask, we tested this with the power off to the poles. It’s obviously induced current from the transmission lines).
The customer assumed that the problem was with our electrical installation, since he did not have this problem prior to our work. Honestly, we kind of feared the same thing. But after quadruple checking every inch of the installation, and replacing all GFCI devices, we felt confident that the problem was not with the installation. We believe it became noticeable after our installation because prior to our work, there was no affective ground path between the floating dock and earth ground. We are thinking that the dock and water were previously at the same potential.
For clarity, there are only two separate 120 volt, 20 amp branch circuits feeding the boat dock. Both originating from a small sub panel on dry land, in a storage shed, approximately 100’ from the water’s edge.
At the customers request, (and because we were running out of ideas), we drove two ground rods on shore, and connected the ramp and all sections of the dock, including the ladder, with braided stainless steel mesh straps. None of this changed anything, nor did we expect it to.
I would appreciate comments and suggestions.