Based on our discussions on loading 3-phase open delta systems with single phase loads it seems there is a need to identify which set of wires is the open phase.
It is import for the electrician to know which set of phase wires / busbars are the open phase so they can make an accurate determination of the load as adding single phase loads to the open phase has more affect on transformer loading than the other two sets.
110.15 Identification of Delta-connected Conductors.High-Leg Marking.
(A) On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded,
only the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is orange in color or by other effective means.
Such identification shall be placed at each point on the system where a connection is madeif the grounded conductor is also present.
(B) On a open delta-connected system where one primary phase winding is not present, the set of conductors or busbars having the open phase shall be permanently marked by an effective means.
The means of identification shall be documented in a manner that is readily available and shall be permanently posted at each point on the system where a service, feeder or branch circuit originate.