For a service.I think the OP is confusing the requirements for connecting the GEC vs where the bonding takes place.
The GEC is allowed to connect anywhere from the weatherhead down to the panel. No mention of first means of disconnect.
For a feeder to a detached building, apparently the GEC is allowed to connect to the feeder EGC anywhere, as per the text quoted from the NEC at the bottom of post #23. So if your feeder goes to, say, 3 panels in a row inside your building, and your last panel is closest to the grounding electrode, you can land your GEC there, rather than in the building disconnect.