Strathead
- Ocala, Florida, USA
- Electrician/Estimator/Project Manager/Superintendent
they are being pedantic.Well, OK, but I would consider a blown fuse to be destroyed since it is no longer functional or reparable.
You need to look at the listing procedures for these devices and see what steps must be followed to get the SCCR and withstand ratings.So what about something like a typical automatic transfer switch?
The ATS manufacturers have tested combinations allowing you to use specific fuses or breakers to support higher withstand ratings.Ok, yes, maybe we are on the same page then. I agree UL508A not only likely contains non passive devices, but the listing process / rules have specific requirements for SCCR and upstream OCPD's that you can't ignore.
What about something like a package HVAC unit, do essentially all of those have a UL 508 panel inside of them?
Yes that is a bad example. I have seen and applied the charts provided with ATS's for various protection types and sizes.The ATS manufacturers have tested combinations allowing you to use specific fuses or breakers to support higher withstand ratings.
ASCO UL1008 Withstand and Closing Ratings (RMS Symmetrical AMP) | Schneider Electric
ASCO UL1008 Withstand and Closing Ratings (RMS Symmetrical AMP)www.se.com
And this is the issue.I guess as far as equipment goes, you would need something that doesnt have a UL508 control panel or any provided SCCR vs OCPD information.
So circling back to the OP and his chiller. Is that likely to have any "restrictions" beyond what the NEC says?And this is the issue.
Yes if it is a listed device. The listing standards will have something to say about the SCCR on the label/data sheets.So circling back to the OP and his chiller. Is that likely to have any "restrictions" beyond what the NEC says?
I don't buy that argument. I mean sure if there is a locked door and for national security reasons Joe Byron (and he is actually awake) and won't let you in so you can't see what is passed it then yeah you say no I can't install a CL fuse because I need to look at the rest of the circuit to see if there are circuit elements that are compatible with this method and since I can't look then I can't do it...One reason you can't just apply a cl fuse to a circuit and claim to lower the AFC is you have no way to know what is installed on that circuit.
If you used a cl fuse to reduce the AFC to say 10k on a circuit, that would allow you to use 10 kaic CBs downstream, but they might not have been tested to work with a cl fuse.
It does not work that way.I don't buy that argument. I mean sure if there is a locked door and for national security reasons Joe Byron (and he is actually awake) and won't let you in so you can't see what is passed it then yeah you say no I can't install a CL fuse because I need to look at the rest of the circuit to see if there are circuit elements that are compatible with this method and since I can't look then I can't do it...
Sorry, absurd argument. It's no different than anything else: we do things all the time where we need to confirm that an existing component or aspect of an electrical system is compatible with what we are doing. And no I am not concerned about someone coming in the future and doing something wrong.It does not work that way.
You have to be able to trust that the AFC labeled on the box you are wiring from is not conditional because it might not be you doing the install down the road
But I think you can put a cl fuse in the feeder circuit of a 508a panel and take advantage of the charts in the supplement to protect the cheap overload.for example, a Square D or Eaton or AB contactor will not be listed in series with a cheap Overload relay that they got from some Chinese supplier that is technically UL listed, but never series tested. Simple little rules like that.
I believe that is correct although the supplement now seems to limit that protection for vfds to branch circuits. You have to read that paragraph very carefully to figure out what they mean.If the device has been tested and listed with a specific fuse, I believe the fuse can be anywhere ahead of it.
petersonraI believe that is correct although the supplement now seems to limit that protection for vfds to branch circuits. You have to read that paragraph very carefully to figure out what they mean.
Read the supplement carefully about the general application of CL devices into the feeder circuit.
It's not in my hands. It is the squirrel murdered by the state of NY.petersonra
I finally was able to focus on your new ICON, bad eyes on my end. Initially I thought it was something WAY different.
What is in your hands live or stuffed?
I have no idea. The charts UL 508a lets you use seem to have some relationship to the fuse let thru current but where it comes from escapes me. You can use the provision with any CL fuse or CB but IME it does not help much above 30 or maybe 60 Amps rating.My thought on the 30A limit.
Are they building in the choke effect of small wire sizes?
If you assume the control panel is at least 30' from the main...200K AFC, X/R of 2, #10 awg CU.
480-3P : Load SCC = 7.3k X/R < 0.09
208-3P : Load SCC = 3.2K X/R < 0.05
I had not heard of that story until now. I like a lot about NY state, but unfortunately it is a police state, being the state with the most police per capita. In theory this isnt necessarily a bad thing, but it does not seem to be possible for the government to focus on actual crime and not harass citizens for petty things when there are large numbers of police.It's not in my hands. It is the squirrel murdered by the state of NY.
You do not understand. The NYSDEC killed the squirrel to protect it.,
You do not understand. The NYSDEC killed the squirrel to protect it.![]()