Yeah, UL 508a 3rd edition has sections SB4.3.2 (current limiting circuit breakers) and SB4.3.3 (current limiting fuses) that allow the short circuit rating of branch circuit components to be raised to the OCPD rated interrupt current, provided the branch circuit components' rated SCCR is no less than the current limiting OCPD's let-through current. Part (b) of each of these sections goes on to stipulate the branch circuit OCPD will be the limiting SCCR component if it's interrupt rating is less than that of the feeder circuit's current limiting OCPD.