Install Current Limiting Fuse to Reduce KAIC
Back to the actual topic of the thread, say I get an electric kiln that contains resistance heating elements, some contactors, and a digital temperature controller, and it is marked SCCR 5 kA. Are those components all "passive"? And if so, does that mean I can install a CL fuse or CL breaker to satisfy 110.10 if my AFC at the equipment would otherwise be greater than 5 kA?
Cheers, Wayne
Cheers, Wayne
The ONLY way you can take advantage of a CL fuse to increase the SCCR of a component is if UL blessed the combination. This blessing will be noted in the instructions or other documentation for the component.
The instructions will tell you what class of CL fuses you can use for a specific part number and the max rating. For instance it may say 30 Amp class CC or 60 Amp class J.
It might also have an entry for a CB. Or it might not. Because it has to be tested with the specific CB, only the contactor manufacturers CBs would be listed if any. They are not going to pay to test their contactors with someone else's CB.
The other problem you may have is that if the kiln comes with a UL listed control panel, nothing you do can change what the SCCR is UNLESS the labeling of the control panel says so. For instance, it might say 5kA but 65 kA with max 30 Amp class J fuses. This is not common.
Cheers, Wayne
While I am clearly not an expert and am struggling with understanding this issue, my take so far:
1. There seems to be vague definitions and standards as to what a CL fuse does to available fault current. Although a CL fuse "reduces the current flowing in a faulted circuit to a magnitude substantially less than that obtainable in the same circuit if the device were replaced with a solid conductor", it seems that a CL fuse does not reduce "available fault current". Those two phrases sound the same to me but apparently they are not?
2. Some equipment that is listed and tested to a product standard will have specific instructions and requirements for SCCR ratings with different ocpds. I suppose it is reasonable that those override any attempts at engineering your own combination. However in your example of a kiln, I do not think there is any testing or product standard that applies.
Code reference?
The other problem you may have is that if the kiln comes with a UL listed control panel, nothing you do can change what the SCCR is UNLESS the labeling of the control panel says so. For instance, it might say 5kA or 65 kA with max 30 Amp class J fuses.
How much equipment has a UL listed control panel? Do most HVAC units and chillers have listed control panels?
I guess what I was driving at with my question was whether there is a category of equipment that is obviously passive and for which you can use a CL fuse to increase the SCCR without any UL testing or information from the manufacturer? Would such entirely passive equipment come have an SCCR in the first place?
Cheers, Wayne
You seem to be reading the NEC definition as applying equally to all items that 'substantially reduced current'. However, not all current limiting fuses are created equal.
Most instructions that list a fuse as protection also include the specific class of fuse required. You cannot use a Class R fuse if the rating requires a Class J. The performance of the fuse is critical to its ability to protect equipment.
Most instructions that list a fuse as protection also include the specific class of fuse required..
Okay but what about things that do not have such instructions and that is not part of any listing or product standard? I like Wayne's approach, let me go even simpler let's just say I install a contactor in a box and it has a 10K sccr.
Back to, is it a Listed contactor or is it a Recognized component?
If it is a recognized component, you can use the let-through curves to chose a fuse which you then submit for testing and Listing. Or you can follow the steps in UL508A, but it would be best if you were authorized to do so. i think 508A pretty much maxes out around 30A Class CC.
Have you tried asking a fuse manufacturer this question? Pick a contactor and a fault current, then ask what fuse they would recommend?
I do not believe there is any NEC requirement for contactors to be listed, although some certainly will be. So if it is not listed, I it seems like it should be fine. If it is listed, does that result in documentation that says ONLY these provided fuse and sccr combinations are allowed? (I admit I have never dug into contactor literature documents).
I have not, perhaps that would be a good exercise.
It seems the confusion is in the definition of "available fault current", which the NEC does not provide. Doesn't a properly selected CL fuse , when used ahead of a passive device, lower the AFC? Unless I am missing something, that is exactly what the NEC definition of CL fuse and the manufacturer literature says it does. Again 240.86 does not apply to a discussion on SCCR, I am not talking about two OCPD's in series.
From the UL's perspective, this is correct. UL allows the SCCR of the downstream devices to be raised to the value of the OCPD, as long as the let-through current of that OCPD is lower than the SCCR of the downstream device. UL specifically states the interrupt rating of any downstream OCPD is unchanged by the inclusion of a current-limiting OCPD in the feeder circuit. (Basically, it doesn't allow series rating of a two OCPD pair.)
Really?
That is not what I saw when I built UL508A control panels. There was no blatant acceptance of any upstream CL device unless we specified it.
Really?
Perhaps it is more accurate to add something like ".....as long as the instructions or product standard for the downstream device does not have specific requirements for the upstream OCPD and it's effect on SCCR."
I do not disagree, however I think there are some things that don't have a product standard or are not listed.
This is a typical spec line on most EE plans ....
"All equipment and materials provided shall be new and (U.L.) Underwriter's Laboratories approved and labeled. "
What items for an electrical install would not carry a UL label?
Doesn't even a 4x4 blank off plate carry a UL?
Not trying to be a SA...just trying to straighten this topic out in my head.
Am I wrong headed in thinking anything with a UL label does not have a product standard?