Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
After reviwing the nec 110.14(C)(1) it is apparent that a lot of electricians have been determing wiring ampacity wrong and or posting incorrely here in mike holts forum.
For example, I recall one post here on Mike Holts forum of an electrician trying to justify assigning a higher ampacity to a wire based on NEC table 310.17.
Although he would appear correcect in doing this for the free air conductor wiring method he claimed to have, it would be incorrect according to the opening wording of NEC code 110.14 (C) (1) which states:
"Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on TABLE 310.16"
on this particular post everybody agreed that he could use this wire and terminate on equipment with the higher rated wire ampacity for conductors in free air
So what would be the purpose of having multiply wire ampacity tables? I believe they would only be useful to start at higher ampacities to be adjusted or corrected lower and used within the ampacity for temperature limits of table 310.16?