You make it sound like one long computation. It's really two separate computations--one is the wire ampacity which just requires looking at 310; the other is termination ampacity, which is covered by 110.14(C).
And sections like 215.2(A)(1) impose different requirements on the necessary values for each--the wire ampacity just has to be at least the calculated load (215.2(A)(1)(b)); while the minimum termination ampacity includes a 125% factor for any portion of the load that is continuous (215.2(A)(1)(a)). Of course, 215.3 imposes a 125% factor on the continuous portion of the load for determining the minimum OCPD size, and then 240.4(B) will require that the wire ampacity be at least 1A more than the next smaller OCPD size (or at least the OCPD size if that is over 800A); either way, that likely is stricter than the requirement of 215.2(A)(1)(b).
Cheers, Wayne