Inspection failed for bonding locknut, NEC code needed please
It has been almost 2 weeks since the failed inspection. And after several emails to the contractor about the failure, he has not replied.
What do I do when the contractor/electrican ghosts me after a failed inspection?
Depending on state law, contact the license board and/or take them to court.
I know this doesn't matter right now because it's too late, but in the future (and for other readers) always withhold final payment till inspections are passed.
You have a few options. Since he's already been paid in full you might have to wait a while for him to return. You can call the inspection authority and explain to them what's going on they should contact the electrician directly and tell him he needs to correct his violation. You could just get another electrician to add a split bonding bushing and call for the re-inspection yourself.
This is usually where pettiness, cost, and the number of failures found during an inspection come into play.
Ultimately, it is the homeowners responsibility to have the inspections completed. Insurance will breathe down your neck if unpermitted work is taking place. Though, the workmanship issues are not the home owners responsibility to resolve if they had a contract with a licensed professional.
I would submit a complaint to the state licensing board. Write a bad review on their yelp, google page, etc.
Ask a lawyer about starting a claim with small claims court or read online about it.
Ask the city to contact the contractor on your behalf.
There are lists that look like the FBIs most wanted. lol. Some states take this more seriously than others. It would also depend on how bad the infraction is.
Then the less petty option is to have a different contractor come out and put the bushing on which shouldn't much cost to you. Pass the inspection. Move on.
Is it your permit or the contractors permit?
If it is your permit it is up to you to pass the inspection. Preferably by having the contractor fix what is wrong, but it can be more challenging when he isn't clearly required to do so. May cost you more to pursue legal actions then it is worth to just hire someone else to fix the problems in some cases.
If it is contractors permit, he can have future issues with the AHJ if he doesn't tend to correct his violations found at inspections.
The contractor is the permit applicant. I did not see the permit until the township called wanting their permit fee. That is when I learned a final inspection was needed and the contractor obviously doesn't do inspections. So I called an inspector recommended by the township.
Obviously you would like to get this resolved but the house isn't going to burn down without additional bonding on the offset nipple. Here in NJ you cannot demand the final payment until after the job passes inspection which is an incentive to ensure that the contractor finishes the job.
I'm surprised at all the back and forth over the strut strap, but no one noticed the single ground rod sticking out of the ground? I'm sure it's not a 10' rod and I don't know the soil conditions, but it probably would require a second rod.
The inspector that failed this should have (or be able to) provide a code citation. No citation = no violation.
A less pleasant question, feel free not to answer, did you already pay in full?
cut the plastic bushing in half with dykes after spinning it off then add a split grounding bushing in its place. Install a bonding jumper from the new bonding bushing to the Neutral boding buss.
Where is the length of raceway mentioned in 352.44? It says expansion and contraction for temperature change in table 352.44
Read the Informational Note for 300.5(J)
Right but we are only talking 4 feet. I don't think you will get an expansion coupling requirement in the OP's situation just from 352.44.
Note to these sections have been rearranged a little bit in 2023.
Table 352.44 gives you, for a given temperature swing, a rate of expansion and contraction. For example, at 100F temperature swing the rate is 4.06" / 100' of conduit. That means that 4' of conduit would change 0.16" in length. So the length is absolutely part of 352.44..
I can you show several photos of PVC pulling out of meter enclosures that are only 4' in length
Obviously due to earth movement, which is covered by 300.5(J), not by thermal expansion/contraction. Even at 100F temperature swing, the thermal length change is below the 1/4" threshold for expansion joints in 352.44. You'd need a 155F temperature swing for an expansion joint to be required in a 4' run of PVC.
Cheers, Wayne
I would be much more concerned about all that exposed SER down by the dirt than a crack in some expanding PVC.
I have been moving away from SE cable after a few complaints like this one where the cable started cracking and peeling after about 6 years:
SER.jpg.
Wait in the bushes outside his house?