sorry, these cables are used for temporary power for a month or so, leave them on floor? trip hazard?Cable tray?
How long are the runs? Is there anything overhead that these can be attached to?sorry, these cables are used for temporary power for a month or so, leave them on floor? trip hazard?
vary from 50' to 200', this is industrial space, there are other conduits to machine overhead, try to meet code for support...How long are the runs? Is there anything overhead that these can be attached to?
Those large zip ties that HVAC monkeys use for ductwork comes to my mind. Either strapped to bar joist or steel or use a two-hole conduit strap to hang it on if it's a wood structureHow long are the runs? Is there anything overhead that these can be attached to?
concrete deck above.Those large zip ties that HVAC monkeys use for ductwork comes to my mind. Either strapped to bar joist or steel or use a two-hole conduit strap to hang it on if it's a wood structure
Possibly use the same 2 hole strap method. What do the existing conduits secure to? Are they on the deck or suspended from rod and strut?concrete deck above.
yes, rod and strut for existing conduit support.Possibly use the same 2 hole strap method. What do the existing conduits secure to? Are they on the deck or suspended from rod and strut?
I think I would probably use large duct zip ties and hang the DLO from the strut.yes, rod and strut for existing conduit support.
will this work for 500KCM wires?I think I would probably use large duct zip ties and hang the DLO from the strut.
I don't see why not.will this work for 500KCM wires?
trip hazard concern?Given the fairly heavy weight of that cable and the amount of labor that would be required to hang it I would opt for the floor option with a temporary cover placed over it.
I've run miles of these cables for load bank testing and the last thing you want to do is try and suspend this stuff in the air if you can avoid it.Nice, will suggest and see what client says. Thank you!
1. Have you suspended this type of cable inside the building? which equipment did you use to hang them?I've run miles of these cables for load bank testing and the last thing you want to do is try and suspend this stuff in the air if you can avoid it.
1. Hanging we would use a Victor split or a strut strap to an existing rack.1. Have you suspended this type of cable inside the building? which equipment did you use to hang them?
2. If running them on floor using southwire product you sent… what is the interval contractor need to secure the cable? every 6 feet or 10 feet?