KWH TO KW- generator sizing

Please don't get caught up in the typo. See post 3 vs post 10. Beo clearly understands the difference between kW, kVA, and kWh.
Thank you kindly, Mr Winnie. Now I have done with this topic.
 
Yeah strange. I thought it was a typo at first, I scrolled back and thought it had been edited to "KWh" but I must have been looking at a different post. He definitely seems to be insisting that KVA is energy.
Without quoting reference posts it is easy to get confused.
Post 3 uses the terms KWn and KW
Post 10 uses the terms KW and KVA.

I would have thought this was a simple typo issue except for post 23 which also says KVA.

I have not seen any editing of any posts, where terms were changed.
 
Ok I think I hope we all can agree:

KWh is energy

KWn is "kilowatt nanoseconds" used to measure large amounts of energy

KW is power

KVA is close enough power
Well, might as well get my two cents in..

KVA and resistance are DC
KW and impedance are AC..

😁
 
Evans a load calculation can be problematic. If all you need to run is a heat pump that has an MCA of 25 amps, a 25 amp generator most likely won't start that hvac unit. Similar issue with any big motors like a well pump.

In most applications, a load calculation will provide a number much larger than needed. My house which has a load calculation of 150+ amps rarely draws more than 30A on a given phase. Most of my appliances are gas though, so that helps a lot. But the air conditioner has a locked rotor amp draw of about 110 amps.

We don't really take LRA into account on residential like this. Well pumps and scroll ACs are not that hard to start and the load calc is so oversized and larger generators have plenty of excess short term capacity to start these things anyway.
 
Evans a load calculation can be problematic. If all you need to run is a heat pump that has an MCA of 25 amps, a 25 amp generator most likely won't start that hvac unit. Similar issue with any big motors like a well pump.

In most applications, a load calculation will provide a number much larger than needed. My house which has a load calculation of 150+ amps rarely draws more than 30A on a given phase. Most of my appliances are gas though, so that helps a lot. But the air conditioner has a locked rotor amp draw of about 110 amps.
This can depend on the prime mover of the generator to a certain extent as well.

I have a portable generator that is rated 8000 watts, but also has a starting capacity rating of something like 12,000 watts. It will start my 3 ton heat pump that suggests MOCP of 45 amp breaker. It won't start it rather instantly like utility power does, it takes a couple seconds. The generator breaker will not hold trying to start this if there is much of anything else for load at the time of starting, but once running you can add other loads .
 