 - Illinois
 - retired electrician
That is not correct. The location of the service point is specified by the utility as any point between their system and the building...premises wiring starts on the load side of the service point. For large services with customer owned transformers, the service point is often the load side of the high voltage fuses. The start of the premises wiring is determined only by the service point, and only your utility can tell you where your service point is.Service Point is defined here as "The point of connection between the facilities of
the serving utility and the premises wiring." Some utility can't just come along and redefine that its a definition in enforceable law.
Premises wiring is always after the meter, and never under exclusive control of the utility.
Where in the NEC does it say who can own a service lateral?
I most definitly own mine, I checked.
For our utility for residential it is defined as the load end of the utility service drop, and for underground residential is it the load side of their service lateral. However, for commercial, the service point is the secondary terminals of the utility transformer that supplies the building. In these cases the building is supplied by overhead or underground service conductors.
Because of cost avoidance, more utilities are specifying the service point as the secondary side of their transformer.Service Point.
The point of connection between the facilities of the serving utility and the premises wiring. (CMP-10)
Informational Note:
The service point can be described as the point of demarcation between where the serving utility ends and the premises wiring begins. The serving utility generally specifies the location of the service point based on the conditions of service.