I have a 50 amp on it now with #6 copper running from the disconnect to the tub. The part that sucks is that this hot tub already had the circuit pre-wired and it is only a 50 amp wire feeding it from the main panel, so it would really suck to run a bigger wire and have to abandon what the owner already paid for.I don't think thats a 110.3(B) requirement but what size breaker and wire are you thinking?
It might be fine on a 50A I would not go higher than a 60A I have never seen a 70A GFCI. The GFCI part does not care, I'd go with mfr recommendation, or calculate the load for the branch circuit per 210.19 / 210.20.
The 60A is probably more to do with the motors, you'd have to add them all up to see.
The pump is probably the only continuous load.
I see. Yeah it probably has a blower motor and a pump motor. What did they pre-wire #6 SER?I have a 50 amp on it now with #6 copper running from the disconnect to the tub. The part that sucks is that this hot tub already had the circuit pre-wired and it is only a 50 amp wire feeding it from the main panel, so it would really suck to run a bigger wire and have to abandon what the owner already paid for.
yesI see. Yeah it probably has a blower motor and a pump motor. What did they pre-wire #6 SER?
It's #6 aluminum from the panel to the disconnect.With #6 Cu, even NM, you would not need to change the wire with a 60 amp breaker
Yep. That's a different story. As others have stated, there no reason not to use the 50 amp.It's #6 aluminum from the panel to the disconnect.
doesn't the nameplate account for all of this (motors)?I don't think thats a 110.3(B) requirement but what size breaker and wire are you thinking?
It might be fine on a 50A I would not go higher than a 60A I have never seen a 70A GFCI. The GFCI part does not care about OCPD size.
I just looked up the current version of UL 1563 and section 71.1 (page 114) says the marked supply circuit ampacity shall be 125% of the current rating of the product and it does not mentions 125% of a motor so it appears UL requires 125% of everything.I've dealt with this several times.
48V X 125% = 60A
40V X 125% = 50A
So if the tub specs say 40A, it gets a 50A breaker
48A gets a 60A breaker
I've never actually measured current on them, I just go by the running amps as stated.
The heading is cut off in your photo. Does it say recommended or required conductors?hes just stating since the instruction of the tub says use #6 copper the feeder to the disconnect must also be copper
Even the feeder to the disconnect huh? What if it was a 100 amp subpanel feed with aluminum and the tub was wired from there? Would that not be allowed either?So yes copper is required if the instructions are part of the listing of the equipment.
IMO the required conductors are only for the branch circuit portion not a feeder.Even the feeder to the disconnect huh? What if it was a 100 amp subpanel feed with aluminum and the tub was wired from there? Would that not be allowed either?