I have a 50 amp on it now with #6 copper running from the disconnect to the tub. The part that sucks is that this hot tub already had the circuit pre-wired and it is only a 50 amp wire feeding it from the main panel, so it would really suck to run a bigger wire and have to abandon what the owner already paid for.I don't think thats a 110.3(B) requirement but what size breaker and wire are you thinking?
It might be fine on a 50A I would not go higher than a 60A I have never seen a 70A GFCI. The GFCI part does not care, I'd go with mfr recommendation, or calculate the load for the branch circuit per 210.19 / 210.20.
The 60A is probably more to do with the motors, you'd have to add them all up to see.
The pump is probably the only continuous load.
I see. Yeah it probably has a blower motor and a pump motor. What did they pre-wire #6 SER?I have a 50 amp on it now with #6 copper running from the disconnect to the tub. The part that sucks is that this hot tub already had the circuit pre-wired and it is only a 50 amp wire feeding it from the main panel, so it would really suck to run a bigger wire and have to abandon what the owner already paid for.
yesI see. Yeah it probably has a blower motor and a pump motor. What did they pre-wire #6 SER?
It's #6 aluminum from the panel to the disconnect.With #6 Cu, even NM, you would not need to change the wire with a 60 amp breaker
Yep. That's a different story. As others have stated, there no reason not to use the 50 amp.It's #6 aluminum from the panel to the disconnect.
doesn't the nameplate account for all of this (motors)?I don't think thats a 110.3(B) requirement but what size breaker and wire are you thinking?
It might be fine on a 50A I would not go higher than a 60A I have never seen a 70A GFCI. The GFCI part does not care about OCPD size.
I'd go with mfr recommendation, or calculate the load for the branch circuit per 210.19 / 210.20.
The 60A is probably more to do with the motors, you'd have to add them all up to see.
The pump is probably the only continuous load.
I just looked up the current version of UL 1563 and section 71.1 (page 114) says the marked supply circuit ampacity shall be 125% of the current rating of the product and it does not mentions 125% of a motor so it appears UL requires 125% of everything.I've dealt with this several times.
48V X 125% = 60A
40V X 125% = 50A
So if the tub specs say 40A, it gets a 50A breaker
48A gets a 60A breaker
I've never actually measured current on them, I just go by the running amps as stated.