Flygonkick
- Michigan
- Electrician
I have a 2HP 115/230v pump being installed where I work and I wanted to get opinions on if it would be okay to run 208 to the motor or if I should get a step up transformer to 230 or 240
The main reason I'm looking at using the 208 or even a step up transformer is because the 208 panel is within 50 feet of the pump installation and the 120 panel is closer to 100 yards away. Gotta love old school buildings.Since you have 208 available, you probably have 120V as well. If so, I’d run the motor at the low voltage connection.
Operating at 208 will likely operate fine, perhaps with shortened life, but why chance it if you have a proper voltage available?
So no neutral in the 208 panel.The main reason I'm looking at using the 208 or even a step up transformer is because the 208 panel is within 50 feet of the pump installation and the 120 panel is closer to 100 yards away. Gotta love old school buildings.
I would want to know whether the manufacturer's data has anything to say about it.I wanted to get opinions on if it would be okay to run 208 to the motor. . . .
Maybe how long is it running at FLA or SFA.I would want to know whether the manufacturer's data has anything to say about it.
and I thought it was +-10%A motor made to run in 230 volts should never have less then 95% of nameplate voltages. So 230 × 0.95 = 218.5 volts so it should not be supplied by 208 volts. Too often have been in plants that had 208 volts and during hot summer days measured 190 volts at load side on motor starters. You could install a buck / boost transformer to raise the existing 208 volts to 230 volts.
I have to disagree with 10% + or - of motor nameplate voltage is too high. Did some searching on Google and found a few interesting articles. First ECM MAY 2000 had an interesting article by Mr Ed Cowern that stated a 10% voltage reduction reduces starting torque to only 81% which would be a problem for a motor with a full.load. NEMA MG1. 12.44 recommends a maximum of 6% + or - of motor nameplate voltage.Check with the MFG. I always say within 10% of nameplate. Some motors rated 230/240 are also marked "suitable for use on 208 volt" but that may have been 3 phase
208v nominal voltage, see actual voltage variation on motor terminals within nema10%+_ motor nominal 230vI have a 2HP 115/230v pump being installed where I work and I wanted to get opinions on if it would be okay to run 208 to the motor or if I should get a step up transformer to 230 or 240
There a 230V motors everywhere running on 208V. Most of them say you can use them at 208V on the nameplate. It's rare to find one that has a problem, and the ones that do it is usually a problem caused by something other than the motor.I have to disagree with 10% + or - of motor nameplate voltage is too high. Did some searching on Google and found a few interesting articles. First ECM MAY 2000 had an interesting article by Mr Ed Cowern that stated a 10% voltage reduction reduces starting torque to only 81% which would be a problem for a motor with a full.load. NEMA MG1. 12.44 recommends a maximum of 6% + or - of motor nameplate voltage.