I have a 2HP 115/230v pump being installed where I work and I wanted to get opinions on if it would be okay to run 208 to the motor or if I should get a step up transformer to 230 or 240
The main reason I'm looking at using the 208 or even a step up transformer is because the 208 panel is within 50 feet of the pump installation and the 120 panel is closer to 100 yards away. Gotta love old school buildings.Since you have 208 available, you probably have 120V as well. If so, I’d run the motor at the low voltage connection.
Operating at 208 will likely operate fine, perhaps with shortened life, but why chance it if you have a proper voltage available?
So no neutral in the 208 panel.The main reason I'm looking at using the 208 or even a step up transformer is because the 208 panel is within 50 feet of the pump installation and the 120 panel is closer to 100 yards away. Gotta love old school buildings.
I would want to know whether the manufacturer's data has anything to say about it.I wanted to get opinions on if it would be okay to run 208 to the motor. . . .
Maybe how long is it running at FLA or SFA.I would want to know whether the manufacturer's data has anything to say about it.
and I thought it was +-10%A motor made to run in 230 volts should never have less then 95% of nameplate voltages. So 230 × 0.95 = 218.5 volts so it should not be supplied by 208 volts. Too often have been in plants that had 208 volts and during hot summer days measured 190 volts at load side on motor starters. You could install a buck / boost transformer to raise the existing 208 volts to 230 volts.