Is 208v acceptable in a 2hp 115/230v motor
Flygonkick
Michigan
I have a 2HP 115/230v pump being installed where I work and I wanted to get opinions on if it would be okay to run 208 to the motor or if I should get a step up transformer to 230 or 240
Since you have 208 available, you probably have 120V as well. If so, I’d run the motor at the low voltage connection.
Operating at 208 will likely operate fine, perhaps with shortened life, but why chance it if you have a proper voltage available?
The main reason I'm looking at using the 208 or even a step up transformer is because the 208 panel is within 50 feet of the pump installation and the 120 panel is closer to 100 yards away. Gotta love old school buildings.
So no neutral in the 208 panel.
In that case, I agree with others - run it on 208V. I would check the running amps after startup to confirm they are not greater than the service factor amps.
It completely depends on the load placed on the motor.
If the motor is lightly loaded, no worries, current will be way under the rating.
Something like a small Honda generator with a knob that could be dialed back to 208 volts is one way to test this before going to all the trouble to construct it.
A motor made to run in 230 volts should never have less then 95% of nameplate voltages. So 230 × 0.95 = 218.5 volts so it should not be supplied by 208 volts. Too often have been in plants that had 208 volts and during hot summer days measured 190 volts at load side on motor starters. You could install a buck / boost transformer to raise the existing 208 volts to 230 volts.
and I thought it was +-10%
The data plate is a good place to start. This propane pump is rated for 208/230.
Check with the MFG. I always say within 10% of nameplate. Some motors rated 230/240 are also marked "suitable for use on 208 volt" but that may have been 3 phase
I have to disagree with 10% + or - of motor nameplate voltage is too high. Did some searching on Google and found a few interesting articles. First ECM MAY 2000 had an interesting article by Mr Ed Cowern that stated a 10% voltage reduction reduces starting torque to only 81% which would be a problem for a motor with a full.load. NEMA MG1. 12.44 recommends a maximum of 6% + or - of motor nameplate voltage.
But NEMA says +-10%.
So what gives here?
208v nominal voltage, see actual voltage variation on motor terminals within nema10%+_ motor nominal 230v
There a 230V motors everywhere running on 208V. Most of them say you can use them at 208V on the nameplate. It's rare to find one that has a problem, and the ones that do it is usually a problem caused by something other than the motor.