208 three phase
St. Louis
Maintenance electrician
208 a phase A 10 amps phase B 5 amps neutral amps = ??????????????????????????????????????????????????????????????????????????????????????
He only gave amps for phase a and phase b. I don't see phase c being used. 2 hots and a neutral. For that portion of the circuit only will the neutral not see a 5 amp load?
The answer the test question probably wants is SQRT of I^A+I^B - (IA IB)
For a fun read see the thread from long ago and use two of the phases
Same here, assuming the currents are 120° from each other.
You are mathematically correct but if the service is built with metal conduit and you check it at the panel you will always read lower as much as 30% !
9/10 ECs running for their nearest app because they can't calc this simple equation. 208V pretty much confirms 3P wye, USA. GD rage baiting with no C load.