208 a phase A 10 amps phase B 5 amps neutral amps = ??????????????????????????????????????????????????????????????????????????????????????
Not for a wye systemIf it is single phase 2 hots and a neutral Phase A 10 amps phase B 5 amps the neutral carries the imbalance which is 10-5=5 amps.
THREE PHASE208 a phase A 10 amps phase B 5 amps neutral amps = ??????????????????????????????????????????????????????????????????????????????????????
You don't have to yell. What is the load on phase C if they are using 3 phase. The post title says three phase but he is only using 2 legs and a neutral.THREE PHASE
If it is a three phase circuit, then it’s unsolvable without knowing what C phase current is.THREE PHASE
Additionally you would need to know the phase of the currents/power factors of the loads.it’s unsolvable without knowing what C phase current is.
Same here, assuming the currents are 120° from each other.0 load on C phase I get 8.7 amps on the neutral.
In a wye configuration they areSame here, assuming the currents are 120° from each other.
If you have loads with various power factors, they may not be.In a wye configuration they are
Three phase source, single phase load?THREE PHASE
You are mathematically correct but if the service is built with metal conduit and you check it at the panel you will always read lower as much as 30% !Same here, assuming the currents are 120° from each other.