Are you asking about ground fault protection for people or just ground fault protection in general?
Very generally speaking on our typical grounded AC system in the US (TN-S) a plain inverse time breaker will provide some type of 'ground fault protection'.
A inverse time breaker generally trips in 2 cycles at three times its handle amps thats the Ground Fault Protection,
so a 30A breaker will trip instantly at a ~90A ground fault.
I dont see a personnel shock protection issue with a grounded fixed appliance connected to a wiring method that contains a equipment ground, as any fault should be cleared in ~2 cycles (33ms).
unless its a people protection issue like article 680.
It perplexes me why they think any grounded appliance needs 5mA GFCI people protection, though I could see an argument for ground fault protection of residential equipment at lower thresholds than a inverse time breaker provides, but not 5mA more like 30mA.