UL 943 has been changed and specifies the trip points for high frequency leakage current. As the current goes up the trip point also goes. They can do this because as the frequency goes up, it takes more current to cause harm to the human body.
The standard applies to both breakers and receptacles, so I assume both will be available at some point.
UL 943 does not require that all GFCIs be of the HF type so the manufacturers can continue to make and sell the standard ones. The 943 committee was split on requiring all GFCIs to be of the HF type, and it is not required. I think over half of us on the committee voted for all to be HF, but just like a code change, it takes a 2/3s majority to make a change in a product standard.