wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
And so to be explicit, the Southwire calculator gives you different results for 120V 3% VD 30A 350' 1.0 PF if you choose Commercial 60C (#1 AWG Cu) vs Commercial 75C (#1/0 AWG Cu), which is not reasonable.The calculator is increasing the resistance/kft with increasing insulation temperature. Which would be accurate if you were specifying operating temperature, but the actual operating temperature won't depend on the insulation temperature.
Cheers, Wayne