1000V systems and voltage rating of EGC wire

don_resqcapt19

Moderator
Staff member
Location
Illinois
Ok fair enough. Only 5 thru 7 override 1-4 correct? We still have a direct conflict and in that case I would go with the statement in 250 that specifically addresses egc's
I agree....where there is a conflict, I apply the most specific rule. In this case that would be the rule in Article 250.
 