1000V systems and voltage rating of EGC wire

Status
Not open for further replies.
In article 250 it says an egc can be insulated or bare. Doesn't that then override the statement in 300.3? 300. 3 should have an exception mentioning this no?
There is nothing in the code that says what overrides what where you have rules in Chapters 1-4 that conflict.
 
Ok fair enough. Only 5 thru 7 override 1-4 correct? We still have a direct conflict and in that case I would go with the statement in 250 that specifically addresses egc's
I agree....where there is a conflict, I apply the most specific rule. In this case that would be the rule in Article 250.
 