In article 250 it says an egc can be insulated or bare. Doesn't that then override the statement in 300.3? 300. 3 should have an exception mentioning this no?
There is nothing in the code that says what overrides what where you have rules in Chapters 1-4 that conflict.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Ok fair enough. Only 5 thru 7 override 1-4 correct? We still have a direct conflict and in that case I would go with the statement in 250 that specifically addresses egc's
I agree....where there is a conflict, I apply the most specific rule. In this case that would be the rule in Article 250.
 