I'm not getting any of the answers listed. Breakers 1,2,7,8,13 and 14 are all A phase, yes? So
Circuit #1 = 2100VA/
Circuit #2 = 41,3000VA
Circuit #7 = Not used
Circuit #8 = Not used
Circuit #13 = 31,300VA
Circuit #14 = 22,000VA
-------------------------------------
Circuit #1 is L-N, so 2100/120 = 17.5A
Circuit #2 3ph, so 41,300/208/rt3 = 114.64A
cIRCUIT #13 is 3ph, so 31,300/208/rt3 = 86.88A
Circuit #14 is L-L, so 22,000/208 = 105.77A
total 324.79A, which is close to F, but not exact... is rt3 1.73, 1.732, or actual value, only rounded at the end? Is F even the right answer?
Circuit #1 = 2100VA/
Circuit #2 = 41,3000VA
Circuit #7 = Not used
Circuit #8 = Not used
Circuit #13 = 31,300VA
Circuit #14 = 22,000VA
-------------------------------------
Circuit #1 is L-N, so 2100/120 = 17.5A
Circuit #2 3ph, so 41,300/208/rt3 = 114.64A
cIRCUIT #13 is 3ph, so 31,300/208/rt3 = 86.88A
Circuit #14 is L-L, so 22,000/208 = 105.77A
total 324.79A, which is close to F, but not exact... is rt3 1.73, 1.732, or actual value, only rounded at the end? Is F even the right answer?