190818-1604 EDT
ron:
I think the autotransformer is the better approach.
Why? If I parallel two Honda 2200s I get 4400 capability at 120 V. Adding a 120 to 240 autotransformer makes 120-0-120 available. Adequately sized I can supply up to a maximum of 4400 on either 120 phase or 240 in any combination that does not exceed 4400 total load.
No isolarion is required, and therefore with an autotransformer you can get the the 4400 capability in any combination with less transformer weight than an isolation transformer.
In a home application there is a continuously varying load between the two phases. If you parallel the two phase circuits, then any combination of loading to 4400 is possible at 120 V, but no 240 V.
.