190914-1132 EDT
Some additional thoughts.
When a generator starts up, if it sees no existing terminal voltage, then it says I am the master and sets an internal memory saying so. Thereafter it is in a master mode that defines frequency, and no load voltage. Both the frequency and no load voltage can be invariant values, but their values are defined within this master generator.
Then the inverter of the master can synthesize an internal impedance that is relatively non-dissipative. This is done by changing the generated voltage as a function of load current. This would be some reasonable value. Possibly 5% from no load to full load. If an external power source parallels this master, then the voltage would rise because the external source is supplying some power, and the master would supply less power and current.
When a slave generator is added, then a self balancing occurs based on the synthesized internal impedances. This I have to think about a little more.
.
Some additional thoughts.
When a generator starts up, if it sees no existing terminal voltage, then it says I am the master and sets an internal memory saying so. Thereafter it is in a master mode that defines frequency, and no load voltage. Both the frequency and no load voltage can be invariant values, but their values are defined within this master generator.
Then the inverter of the master can synthesize an internal impedance that is relatively non-dissipative. This is done by changing the generated voltage as a function of load current. This would be some reasonable value. Possibly 5% from no load to full load. If an external power source parallels this master, then the voltage would rise because the external source is supplying some power, and the master would supply less power and current.
When a slave generator is added, then a self balancing occurs based on the synthesized internal impedances. This I have to think about a little more.
.