190821-2220 EDT
fastline:
Good.
Borrow a second Honda, and connect both Ns together. Run both generators with no other connection other than the Ns. Measure L1 to L1 with a Simpson 260 in either AC or DC. With the Simpson you can see 1 Hz or lower variations. With a Fluke 27 it is not very distinguishable what is hapening until you get to lower difference frequencies. I used a function generator to generate a sine wave for the Simpson and Fluke tests.
I am guessing that a small autotransformer may provide sync between the two generators when unloaded. You might want to fuse the autotransformer to protect it in the test.
.
fastline:
Good.
Borrow a second Honda, and connect both Ns together. Run both generators with no other connection other than the Ns. Measure L1 to L1 with a Simpson 260 in either AC or DC. With the Simpson you can see 1 Hz or lower variations. With a Fluke 27 it is not very distinguishable what is hapening until you get to lower difference frequencies. I used a function generator to generate a sine wave for the Simpson and Fluke tests.