This is more of a thought why these days might be a good idea to use 14/4 Romax for a shared neutral circuit one white and one gray
 
If the circuits are on a GFCI and/or AFCI breaker, you will either need separate neutrals or a 2 pole breaker. This relates to your other thread. It is a design decision.
 
I'm in favor of these cables (12-2-2) for AFCI/GFCI home runs especially for things like the kitchen where you'll need multiple 20 amp circuits.
 
If the circuits are on a GFCI and/or AFCI breaker, you will either need separate neutrals or a 2 pole breaker.
While that always applies to GFCIs, in many cases two single pole AFCIs with handle ties can be used for a multiwire branch circuit.
 