That doesn’t make sense. If you have 2 neutrals, the circuits don’t
Sounds good. I will keep that in my notesIf the circuits are on a GFCI and/or AFCI breaker, you will either need separate neutrals or a 2 pole breaker. This relates to your other thread. It is a design decision.
While that always applies to GFCIs, in many cases two single pole AFCIs with handle ties can be used for a multiwire branch circuit.If the circuits are on a GFCI and/or AFCI breaker, you will either need separate neutrals or a 2 pole breaker.
14-2-2 instead of 14-4 (Infinity mentioned 12-2-2, which would be the 20 amp version)This is more of a thought why these days might be a good idea to use 14/4 Romax for a shared neutral circuit one white and one gray
Good point….now that the GFCI function has been removed from AFCIs.While that always applies to GFCIs, in many cases two single pole AFCIs with handle ties can be used for a multiwire branch circuit.
Correct thank you14-2-2 instead of 14-4 (Infinity mentioned 12-2-2, which would be the 20 amp version)
14-4 would almost certainly be black, white, red and BLUE
14-2-2 is black, white, red, and WHITE w/ red tracer