2 pole 125V receptacle

Status
Not open for further replies.

Jamesco

Senior Member
Location
Iowa
Occupation
Master Electrician
I have drawings which show 2 pole 125V receptacle. It is similar to link shown below. Panel schedule show 2 pole breaker with 2 conductors and 1 equipment ground conductor.

Maybe a stretch, is the power system a 120V Isolated Power System by chance? That would explain the 2 pole breaker.
 

jap

Senior Member
Occupation
Electrician
I think the misunderstanding is a simple typo that's getting blown way out of proportion on this thread.

JAP>
 

kwired

Electron manager
Location
NE Nebraska
Specific model number is not listed however drawing says 20A, 125V, 2P, 3W receptacle
Many tables and charts and even packaging will often state 2P, 3W : 3P, 4W : 4P, 5W. Then you get into a little less common configurations that may be 3P, 3W or 4P, 4W - which would be devices that do not have an EGC included in the connections. Old 3 wire range or dryer receptacles would technically be 3P, 3W there is no EGC on those even though the code allowed you to bond the neutral to the frame of the appliance.
 