. Unlicensed electrician tampered with the meter and "upgrade" the service, he installed a new service panel, . . . . .
Here are the pictures, he's good, he used AWG 12 for all the receptacles jumpers and because the panel is closed to the water heater he left the meter without cover for ventilation purposes (this is the problem with meter electronic reading, no one notice it) Ah, he is too generous that he provided 14 disconnects instead of a main. That lady paid only $2,500.00 for that wonderful upgrade
Well sure, if you are going to get all picky and stuff. :grin:That receptacle is wired reverse polarity
I will guarantee that there is not one strictly residential electrical van in the entire Washington DC area that has a piece of gray THHN in it!:grin:
.. I think POCO missed too many violations to their meters because of those electronic readers.
Some of the wireless readers will tell POCO if power has been lost (like from pulling the meter from the socket).
We have one POCO that if you pull a meter without calling first will notify them fairly quickly and they will dispatch someone to investigate the outage.
There are other colors?If strictly residential they probably have no more than black, red, white, and green for THHN conductors.
There are other colors?![]()
Wow there is enough violations in the meter and panel alone to keep you bussy for a few days
Meter too high for most POCO requirments
No bonding bushing on metal raceway between meter and panel
I can't see any visable grounding electrode conductors in the panel
No main service disconnect, required for a lighting and branch circuit panel 408
Pipe running out of the bottom of panel looks way over wire count as with maybe others
use of a non WP box and fittings in an outdoor damp location
possable a 110.26 violation on panel but angle of camera is hard to tell
At least the wires in the panel are installed in a neet maner.:grin: