Article 404.2(C) is trying to provide for a future installation.
Doesn't this contradict 90.1(B)?
I think so, I do not think it could not be more contradictory.
Article 404.2(C) is trying to provide for a future installation.
Doesn't this contradict 90.1(B)?
My boss happens to be on that code making panel.
I believe a big part of the reason for requiring the neutral was to discourage the manufacturing of products like this, http://www.smarthome.com/36529/Levi...ner-Wall-Switch-Occupancy-Sensor-White/p.aspx, which actually use the EGC in place of the neutral. From what I understand, these are approved for single replacements, but when you replace more than one switch, you start adding more and more current on the EGC.
My boss happens to be on that code making panel.
I believe a big part of the reason for requiring the neutral was to discourage the manufacturing of products like this, http://www.smarthome.com/36529/Levi...ner-Wall-Switch-Occupancy-Sensor-White/p.aspx, which actually use the EGC in place of the neutral. From what I understand, these are approved for single replacements, but when you replace more than one switch, you start adding more and more current on the EGC.
The hope is that future sensor designs will be such that manufacturers will expect a neutral at the switch location and design them appropriately, instead of the current workaround they have.
It's not a perfect solution, but it's an attempt to nip the problem in the bud before it even gets worse, as energy savings code will rely more and more on the use of these types of devices.
To me the type of thinking above is completely backwards.
If we need a neutral we pull one, if we dont need one we dont.
but it shouldnt be a violation if we dont pull one when one is not needed at that time.
The way to nip it in the bud is to tell the manufacturers that if thier device requires a neutral then they need to manufacture it as such, and not use the ground wire as a substitute for a neutral.
that could exclude quite a few switches all by itself" or the switch is not within the lit area .."
Exception No. 2: Where multiple switch locations control the same lighting load in an interior
room or space, a grounded conductor of the lighting circuit shall not be required at each such
location if one has been provided at one or more switching points that is (are) visible from most
areas within the room including all principal entry points.
Where a switch controls a receptacle
load or lighting load that does not serve a habitable room or bathroom, or where automatic
control of lighting has been provided or the switch is not within the lit area, a grounded circuit
conductor shall not be required.
If you don't agree with it then don't pull it. Tell the inspector that you are not going to pull it and he can just deal with it.
Then stand back and watch how he deals with it.
My guess is you will be pulling it or your customer or your bosse's customer won't be moving in.
Besides unless your state has already adopted 2011 it's a moot point until they do.
Lots of things in the NEC I don't agree with but we wire to the code wether we agree with it or not.
Explain please. Are you saying a DPST switch? what is the reasoning behind this?
It's gonna get crowded in jamb switch boxes.
That would be a good exception to the code.
Done-- I sent it in.
Proposal 404.2(C) exception (3) Boxes used for lights controlled by a door jamb switch.
Substantiation: These door jamb switches are very tiny and adding another wire will make it more difficult for wire fill. It also is unnecessary as an electronic controller cannot be used in jamb switch boxes anyway.