"Ferris Bueller, you're my hero!"Done-- I sent it in.
"Ferris Bueller, you're my hero!"Done-- I sent it in.
Done-- I sent it in.
Proposal 404.2(C) exception (3) Boxes used for lights controlled by a door jamb switch.
Substantiation: These door jamb switches are very tiny and adding another wire will make it more difficult for wire fill. It also is unnecessary as an electronic controller cannot be used in jamb switch boxes anyway.
Can these be submitted electronically ?Exception No. 2: Where multiple switch locations control the same lighting load in an interior
room or space, a grounded conductor of the lighting circuit shall not be required at each such
location if one has been provided at one or more switching points that is (are) visible from most
areas within the room including all principal entry points.
Where a switch controls a receptacle
load or lighting load that does not serve a habitable room or bathroom, or where automatic
control of lighting has been provided or the switch is not within the lit area, a grounded circuit
conductor shall not be required.
Not sure I agree with the MA amendment. Although I feel the NEC is a design issue and should not exist, I do think in the spirit of the rule that the amendment would not hold water. If I remember correctly there are many switches out there for multiple switching that need a neutral at each location.Hey Dennis , while you pen is warm why not try to get the Mass exception through?
Absolutely, just download the form in Word and then submit it to the email address at the bottom of the form.Can these be submitted electronically ?
Not sure I agree with the MA amendment..........
It's gonna get crowded in jamb switch boxes.
No.Article 404.2(C) is trying to provide for a future installation.
Doesn't this contradict 90.1(B)?
90.1(B). . . not necessarily . . .for. . .future expansion of electrical use.
No.
Not necessarily but it can be.
I guess the most they are saying is it won't interfere with future expansion.
Also if conduit is used then a neutral need not be present.
Neither, is it required if there is crawl space or attic access.
404.2 Switch Connections.
"(C) Exception: The grounded circuit conductor shall be permitted
to be omitted from the switch enclosure where either
of the following conditions in (1) or (2) apply:
(2) Cable assemblies for switches controlling lighting
loads enter the box through a framing cavity that is
open at the top or bottom on the same floor level, or
through a wall, floor, or ceiling that is unfinished on
one side"
Did you get yourself a code book yet or are you still posting about what you have not read?
Thom I must disagree with you on that. The access must be on the same level.
Doesn't the "or" differentiate whether the box is accessible from attic/crawlspace vs. unfinished ceiling/wall/floor?? I agree with you on the "same level" wording, but it would hardly be the first time NEC wording was questioned. :grin:
Doesn't the "or" differentiate whether the box is accessible from attic/crawlspace vs. unfinished ceiling/wall/floor?? I agree with you on the "same level" wording, but it would hardly be the first time NEC wording was questioned. :grin: