al hildenbrand
Senior Member
- Location
- Minnesota
- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
:?:?True but that does not relieve the requirement for the receptacle to be AFCI protected
You say "True".
Did you read the exception to 2014 210.12(B)? It says flatly, "AFCI protection shall not be required. . . "