- Location
- Massachusetts
And, even if you could document CMP intent, the intent, if different from the language in the published and adopted-into-law NEC wins in court, hands down.
Can you cite a case?
And, even if you could document CMP intent, the intent, if different from the language in the published and adopted-into-law NEC wins in court, hands down.
Can you cite a case?
Can you cite a case?
Well, no. And I suppose a really good lawyer or team of lawyers can do just about anything. . .
How can you assure me? Document it. I see absolutely no "intent" being adopted into enforceable ordinance. . . only the NEC itself.
And, even if you could document CMP intent, the intent, if different from the language in the published and adopted-into-law NEC wins in court, hands down.
I don't see the issue with saying " Elsewhere" in the code.
From the CA electrical code
(4) Arc-Fault Circuit-Interrupter Protection. Where a
receptacl outlet is supplied by a branch circuit that
requires arc-fault circuit interrupter protection as specified
el ewhcre in this Cod, a rcplaccm nl receptacle at Ihis
outlet hall be one of the folio ing
(1) a listed outlet branch _circuit type arc-fault circuit
interupter receplacle
2013 California Electrical Code
(2) A receptacl prolected by a listed outlet branch
circuit type arc-fault circuit interrupter type
receptacle
(3) A receptacle protected by a listed combination type
arc-fault circuit intemlpter type circuit breaker
This requirement becomes effective January I. 2014.
(5) Tamper-Resistant Receptacles. Listed tamper reistant receptacles shall be provided where replacements
are made at receptacle outlet that are required to be
tamper-resistant elsewhere in this Code.
(6) Weather-Resistant Receptacles. Weather-resistant
fec 'ptaclcs hall be provided where replacements are
made at receptacle outlets that arc required to be 0
protected elsewhere in this Code
OK so where is the confusion. SAME WORDING FOR: Wet locations, AFCI , TAMPER.
OK. Take TAMPER, as a case in point. When you come to an existing, legal, two-wire nongrounding-type duplex receptacle on the wall of a kitchen for, say, a wall hung kitchen clock, do you then ignore the 406.4(D)(5) "elsewhere in this Code" and pretend that 406.12 Exception (4) doesn't exist?
You are telling me that because of your certainty of CMP intent that Tamper-Resistant devices MUST be installed inplace of an existing nongrounding-type receptacle. Yet the Code clearly says I can replace a nongrounding-type with a nongrounding-type.
So do you not use 406.12 Exception (4)?
(I am deliberately picking this hypothetical to side step the GFCI and / or AFCI complication while considering only TR.)
OK. Now that is important. The points I am making about 406.4(D) and 210.12 are not concerned with the grounding wiring methods that you experience in most of your work. For grounding wiring methods, I agree with you about replacements.Most if not all the homes or condo's I work on have a grounding connection.
My experience is that old INTACT wiring is defined as decrepit by those that don't like it, and many times don't understand it.Then we have folks like yourself that are trying to keep the inventory of old decreped wiring intact.
My experience is that old INTACT wiring is defined as decrepit by those that don't like it, and many times don't understand it.
Who looses? Not me. The homeowner is suddenly smacked with huge rewire bills, not me. And for what? The old system was electrically sound and intact, and now they have had to pay for it to be removed to be replaced by a new electrically sound and intact system.
Yes.Back in the day I used to think Knob and tube was fine and as long as was properly fused it was ok. I would find the wire fully intact in most instances where it was not overloaded.
There is a long history here of box installation for all non-K&T luminaires. Since 1985, attention to the temperature requirements of modern luminaires have been adhered to.But then you take into consideration light fixtures that cause too much heat and break down the isulation.
As politically correct, and health conscious as that is, it is a non-NEC issue. The grounded service conductor and the main bonding jumper create a more persistent EMF problem.You have high measurable EMF because of the spacing of hots and nuetrals in the wall.
Good minds, here, will argue cogently that adding an equipment grounding conductor increases hazard in wood framed houses.Then there is the lack of a grounding conductor.
Change the box out for the GFCI and use a dimmer that doesn't require a neutral.Too small a box for some dimmers or GFCI, No nuetral for a dimmer
Maybe. But most of the time, the client is only needing a few maintenance things done, and the cost of returning and exchanging the dimmer and accepting that the replacement receptacles are two blade non grounding-type is more than acceptable to their pocket books.Lack of most of which are reason enough to perform a re-wire.
I agree. (And I substitute 2014 NEC in place of "here in CA".) Especially when trying to apply 406.4(D)(4) to existing, remaining, INTACT, electrically-sound, ungrounded wiring methods in well maintained Early 1900s housing stock.I am not saying that when you replace a outlet that is grounds for a re-wire. As I said here in CA there is a provision in the code that allows for some discretion.
And, as for 210.12(B)(2) and the Eaton and Leviton installation instructions, that's also another story altogether (and a thread hijack which I will try to refrain from). The effect of Eaton and Leviton's instructions for the OBC AFCI is to write new more restrictive Code.
As politically correct, and health conscious as that is, it is a non-NEC issue. The grounded service conductor and the main bonding jumper create a more persistent EMF problem.
Good minds, here, will argue cogently that adding an equipment grounding conductor increases hazard in wood framed houses.
I think that the argument must be that the metal will be live but that there will not be any grounded surface for the occupant to touch inside the wood frame house, so no shock risk.What kind of substatiation do you have for such a comment?
Please tell me how a Switch leg with no ground is going to trip a breaker when the conductor is damaged and touching metal piping or something similar.
Same thing with a 220v device that is ungrounded. Tell me what happens when one leg touches the metal of the device.
It will never trip the breaker but the metal will be live.
As politically correct, and health conscious as that is, it is a non-NEC issue. The grounded service conductor and the main bonding jumper create a more persistent EMF problem.
Good minds, here, will argue cogently that adding an equipment grounding conductor increases hazard in wood framed houses.
First of all, those are two different answers to two different situations.What kind of substatiation do you have for such a comment?
I said "equipment grounding conductor" (EGC). Some how you are imagining floating metal from the absence of a branch circuit EGC. That makes little sense.Please tell me how a Switch leg with no ground is going to trip a breaker when the conductor is damaged and touching metal piping or something similar.
Same thing with a 220v device that is ungrounded. Tell me what happens when one leg touches the metal of the device.
It will never trip the breaker but the metal will be live.
Because of the separation between the two current carrying conductors in any circuit, K&T will always produce a higher magnetic field than any modern wiring method.
And even without a grounded metallic raceway a hot and neutral which are in very close proximity will also have a slightly lower electric field at a distance.
Tapatalk!
Don't overlook 300.3(B)(3). Any non ferrous wiring method can create EMF. And if one adheres to 300.20(B) one can create even more situations creating EMF in the occupancy.Because of the separation between the two current carrying conductors in any circuit, K&T will always produce a higher magnetic field than any modern wiring method.
Again, 300.3(B)(3) does not require this. As I said, EMF is not a NEC issue, and the NEC required service configuration for conventional residential single phase 120 / 240 Volt services guarantees persistent EMF sources.And even without a grounded metallic raceway a hot, EGC, and neutral which are in very close proximity will also have a slightly lower electric field at a distance.