I've been in consulting engineering for almost 4 years now and still am having troubles with something that should be simple. When entering wattages/amperage into panel schedules, I seem to always get confused with 208/1 and 480/1 loads when I have three phase service. Could someone please help me with this? It's been described to me before, but just has never clicked.
For example:
Load of 2228W on at 208V/1 circuit. So it's a 20/2 pole breaker on two of three phases. Do I:
1) 2228W/208V=10.7A and put 10.7A on the two phase.
2) 2228W/120V=18.56A and then divided by two to have 9.28 on the two phases.
I'm pretty sure, based on the company panel schedule calculations, I do the second method; but I'm getting confused as to why.
Thanks.