No. Sorry for not specifying. I automatically assume there to be no neutral on 2-pole circuits UON.iwire said:I don't think you gave enough info.
Are we to assume circuits 9-11 and 13-15 also utilize a neutral?
Through the breaker and branch circuit itself the current is 16A. When the current "arrives" at the bus bars it meets up with out-of-phase currents which have both an adding and cancelling effect. This is similar to how line-neutral currents balance out where they meet up with out-of-phase neutral currents. However, with phase conductors the angles of line-line loads aren't 120? out-of-phase with the source angle. They are ?30? out-of-phase... so only a partial "cancellation" occurs. Perhaps this is an oversimplification of the issue, but I find it suffices for practical application.If not I want to know how one side of a two pole breaker draws more than the other?
I must say I understand very little of how this occurs, but I do get a better understanding every time I run across reliable information. Haven't been pressed enough to actually buy a book that elaborates on the issue, though.