Refering to an older thread.
ray94553 on March 04 said:
Using methods and calculations that everyone in the industry knows and understands is the whole purpose of the Code. Isn't that why it is there? See; National Electric Code Examples D5(a) and D5(b). ..Why would you want me to use methods or calculations that were not standard to the industry? Arguing an issue as a point of theory is all fine and good but to implement your pet methodologies without warrant is a violation of the ideals of a uniform standard.
Those who arrived at 9.28A for this 208v 2228W load, have each cited different publications that guided their preference for the balanced results, using Pφ = Vφ* Iφ* cos(θ), or I? = P? / Pf / E?, rather than I = P/V.
1) ray94553 offers "Introductory Circuit Analysis 6th Edition by Robert L Boylstead ? 1990, Chapter 23"
2) kingpb offers the "Handbook of Electric Power Calculations, by H. Wayne Beaty, third edition, pg 13.9"
3) I also offered the NEC examples ray cited earlier.
Presumably these specific pages and chapters show some proof how values similar to 9.28 were derived, and thats why the citations were offered. If any proof or measurement exists that disputes the 9.28A, or NEC's use of Annex D ex.D(5), I believe this audience is sophisticated enough to recognize them.
When someone told science-fiction writer Theodore Sturgeon that 95% of science fiction was crap, he replied, 95% of everything is crap. This has gone down in science fiction circles as Sturgeon's law
95% of calculated results without proof is also crap. Although, calculation without measurement or proof can be disputed indefinately, the difference is those who rely on reproduceable measurements don't have to use the crap; while those looking exclusively at the numbers are getting people to eat it.