OK, all this is forcing me to delve into symmetrical components, which I did not want to do. I was hoping someone else would step up and provide the details. But, it appears inqusitive minds want to know the answer to this riddle.
BTW: For all those that said
the current through the load is 10.7A are correct, you can all sleep better tonite.
This scenario has stumped many an engineer, designer, and electrician. Some repsonses were getting close, and I thought Steve and Winnie were going to nail it, my hats off to their effort.
I'll give the answer, then explain were it comes from - For a 2228W load connected across 2 phases of a 3 phase 208Y/120V panelboard (and no other load connected) the amount of current that will be seen on the Phase A, and Phase B feeder is: drum roll............................................ 6.2A.
I know, seems impossible, but that is the magic of what we call unbalanced systems, and the reason symmetrical components exist. For anybody that wants to see printed verification, go to the Handbook of Electric Power Calculations, by H. Wayne Beaty, third edition, pg 13.9.
The unbalanced 3-ph circuit total power is the sum of the powers represented by the separate positive, negative, and zero phase sequence products. The input voltages are balanced so the negative and zero sequence voltages become zero, and we are left with the following:
P
tot = 3V
ph1*I
ph1*cos(ang
1)
Becasue the way the angles work out using symetrical components, cos(ang
1) = 1, so, calculating current says: 2228/(3*120) = 6.2A.
Ths has been confirmed using ETAP program, I recommend everyone that has the ability to check this using a program to do so.
Now, for the crux of the issue, if you were to put another 1114W load on Phase C, thereby blalancing the system, the current on each of the feeders goes to 9.3A. Again, I can confirm this using ETAP.
Conclusion: Although you will have 10.7A across the load, you will never see more current on the panel then as if the entire panel is balanced, (i.e. 9.3A versus 6.2A.) This is why for panel sizing I always try to teach people to use a three phase balanced system, and when showing the VA on the panel you need to treat it as balanced, (i.e. divide load by poles and divide by voltage) even though the load current, for sizing the branch circuit may have a higher current at the load. I dont' beleive that many panel schedules treat unbalanced load properly, I know ETAP does.
Plus, it would be a disaster trying to recalculate unbalanced load current on the panel feeder, every time you added a circuit to a panel. Especially for guys in the field. It's easier, and actually more conservative, to treat it as a balanced load.