618electrician
Member
- Location
- St. Louis
- Occupation
- Maintenance electrician
208 a phase A 10 amps phase B 5 amps neutral amps = ??????????????????????????????????????????????????????????????????????????????????????
Not for a wye systemIf it is single phase 2 hots and a neutral Phase A 10 amps phase B 5 amps the neutral carries the imbalance which is 10-5=5 amps.
THREE PHASE208 a phase A 10 amps phase B 5 amps neutral amps = ??????????????????????????????????????????????????????????????????????????????????????
You don't have to yell. What is the load on phase C if they are using 3 phase. The post title says three phase but he is only using 2 legs and a neutral.THREE PHASE
If it is a three phase circuit, then it’s unsolvable without knowing what C phase current is.THREE PHASE
Additionally you would need to know the phase of the currents/power factors of the loads.it’s unsolvable without knowing what C phase current is.
Same here, assuming the currents are 120° from each other.0 load on C phase I get 8.7 amps on the neutral.
In a wye configuration they areSame here, assuming the currents are 120° from each other.
If you have loads with various power factors, they may not be.In a wye configuration they are