Bob now you opened another can of worm's LOL
Bob now you opened another can of worm's LOL
Remember that the above is from the section of 210 that is called "Branch Circuits Required"210.11(C)(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
I do not see anything in either of these that actual requires the 20 amp circuit to feed the washer.210.52(F) Laundry Areas. In dwelling units, at least one receptacle outlet shall be installed for the laundry.
So a 15 amp circuit would comply with this for my washer.210.23(A)(1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.