Re: 210-52(5f)
Best thing to do is buy an apartment and take clothes to laundromat
I agree with Jim !!! Before I expended the amount of energy we've all put into deciding whether to install an additional receptacle off the same 20 amp laundry outlet, tap off the dining room outlet, run a separate 15 amp outlet or run 5 new outlets I'd rather bring my laundry to a laundromat and not have to worry whether the receptacle outlet I'm using is code compliant.
There were a lot of "what if's" posted here :
What if I ran an additional outlet off the dining room circuit ?
There's already a 20 amp branch circuit for the laundry and you would be code compliant if you added an additional receptacle for ironing. If you're that concerned run a 12/3 and add the receptacle outlet off the 2nd phase. The down side is that you eat up another point in the breaker panel and you wouldn't be able to use that outlet for anything else but receptacles in that area. There is some merit to doing this though; whoever the genius was that installed the laundry circuit in my house also installed the dishwasher on the same circuit. I cannot run all 3 appliances at the same time.
What if I tapped off the lighting circuit and installed a 15 amp receptacle ?
Why would you ? There's already a 20 amp circuit for the laundry ?
What if I installed a single receptacle for the washer ?
Why would you ? A single receptacle is more expensive than a duplex. Besides which, if you have a gas dryer wouldn't it be more convenient to plug it into the 2nd half of the duplex or would you install an additional single receptacle ?
Why can't I install a 15 amp receptacle outlet for my washer if that's what the mfr. requires ?
Because the NEC indicates that a 20 amp receptacle outlet is required for a laundry area. Just because a mfr. states that their machine will operate on a 15 amp circuit doesn't make it code compliant to install a 15 amp receptacle outlet (unless it states that the maximum breaker size should be 15 amps - which I've never seen). A washer is not (in many cases) the only appliance component of the laundry area. Dryers are also run off the laundry circuit. And, if you only ran a 15 amp circuit it may not hold if both appliances are running at the same time.
I think we're all guilty of reading too much into what the NEC doesn't state rather than what it does state. By the way, in Article 100 under "definitions" there are no definitions for "area", "room" or "shall". Does anyone know exactly what they might mean with respect to the NEC ? Sounds like an ESL course to me!!!