Smart, I think you're way off base in your reasoning.
210.52(B)(1) says the SABCs shall serve all walls, floors and fridges. It also makes clear that a receptacle behind a fridge is not serving wall space.
Don't confuse required outlets (i.e. location) with outlets (i.e. purpose) permitted to be on an SABC.
210.52(B)(2) says that the SABCs shall serve none else.
True... but the question is: what can be included and what cannot. What is included, other than the exceptions, are "specified in 210.52(B)(1)"... which says "all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment." 210.52(A)(3) says only floor receptacles within 18" of a wall can be counted as serving wall space... and the only mention of floor receptacles therein. So is a middle-of-the-floor receptacle an "other outlet". If you go solely by 210.52(A) general, you cannot install a floor receptacle at 18" or greater distance from a wall... "In every kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area of dwelling units".
The point is is that these are the "required" outlets... and the "in addition to" outlets are not "other outlets".
210.52(A)(1) says that outlets within cupboards are not wall space.
I don't see that...
I'm not saying they are wall space. I'm just saying that 210.52(A)(1) doesn't say that.
210.52(C)(5) says that receptacles rendered not readily accessible by a slew of things are not SABC receptacles, even in an appliance garage.
Quite true... regarding required countertop receptacles.
So a receptacle installed in a cabinet is definitely not a countertop receptacle. I concede :slaphead:
:roll:
I'm sure there's an Annex example (and probably text in 220) that a disposal is taken in addition to the SABC demand load as well.
Well it is a motor-operated appliance. It can be a small apliance and not calculated as a motor load, or vice-versa. I would weigh this according to its size (i.e. HP or equivalent). But if calculated as a motor, I would not be putting it on an SABC, just as if I put it on an SABC I would not calculate it as a motor.
Do you honestly think a disposal can just be straight fed off the SABC? Honest?
Yes... honestly.
Would I? Well now that's a whole different ball game there... and the answer is quite likely next-to-never, given the choice. :angel: