- Windsor, CO NEC: 2017
- Service Manager
(2) Island Countertop Spaces. At least one receptacle shall
be installed at each island countertop space with a long dimension
of 600 mm (24 in.) or greater and a short dimension of
300 mm (12 in.) or greater.
No place does it say no more than one required.
You can lead a fool to the code, God help him learn how to read it.
With your logic, you could say the code "requires 20 outlets" because 20 is greater than zero.
It is exactly that place that clarifies that no more than one receptacle is required on one island.
Does a cord have to pass through the sink to serve either of the taller counter areas if the receptacle is behind the sink? No. Does the cord hang to the floor because there is no counter under it? No.
An island is a chunk of counter with no wall attached to it. There is sufficient counter behind the sink to merge the two halves of the island. The height of the counters is irrelevant, they could be five feet above finished floor and be perfectly fine per the NEC.
Why are we making this difficult?