- Occupation
- Licensed Electrician
More straight to the point, if the code requires GFCI protection for your electric vehicle charger you can't get away from it by saying there is no outlet.
All items covered by art 440 have a hermetic refrigerant compressor in them. No such compressor, then something between 422 and 427 will likely cover it if it is "HVAC" equipment in nature.You won't . As far as I know there are no references to HVAC in the NEC that do not send you to 440.
So by definition individual branch circuit should not exist because it does not mention an outlet point?OK, great. That means the utilization equipment is not part of the branch circuit, right? They are different, disjoint.
Then as the electrons move (to use a simplified model) from the grid, through the premises wiring, through the load, and back to the grid, at some point they leave the branch circuit and enter the utilization equipment (or vice versa) That point is the outlet. That's what the definition says.
Cheers, Wayne
Ryan Jackson does not agree with that anymore!And somewhere between there is an outlet.
We covered that already. Just because you are obsessed with your misinterpretation of "outlet" doesn't mean that every NEC definition that could mention an outlet has to mention it.So by definition individual branch circuit should not exist because it does not mention an outlet point?
Yes, basically, the place where the gods let the electrons out to the equipment.How about "Outlet: the point where utilization equipment connects to premises wiring". I would think that covers it all.
-Hal
Were do outdoor electric infrared heaters come into play with the GFCI rule? Are they exempt until 2026 NEC as they may be considered HVAC? Electric infrared heaters are mounted at the same height or higher than lighting fixtures which are exempt. Has anyone run into this.
If the heaters are controlled by a sub panel with branch circuit protection, fed from the main dist. panel with single phase power no neutral, how would you be able to use GFCI protection without the neutral wire? The control can also be built with fuses and how would you get away with not having gfci protection with fuses? If the heater control panel requires a feed of 50 amps or less, it could be feed with a GFCI breaker in the main panel. But if it is over 50 amps then we cant feed with as GFCI device from the main panel.We covered that already. Just because you are obsessed with your misinterpretation of "outlet" doesn't mean that every NEC definition that could mention an outlet has to mention it.
Since you're just repeating the same wrong arguments without actually engaging or responding to the specifics of what we're saying, then I'd say we're done here.
Cheers, Wayne
Since the rule in question only applies to one and two family dwellings, it extremely unlikely that there would be any panel that does not have a neutral. There are GFCI breakers larger than 50 amps.If the heaters are controlled by a sub panel with branch circuit protection, fed from the main dist. panel with single phase power no neutral, how would you be able to use GFCI protection without the neutral wire? The control can also be built with fuses and how would you get away with not having gfci protection with fuses? If the heater control panel requires a feed of 50 amps or less, it could be feed with a GFCI breaker in the main panel. But if it is over 50 amps then we cant feed with as GFCI device from the main panel.
That is 100% false. I just spoke to him the other day on this issue.Ryan Jackson does not agree with that anymore!
The control panel for the heaters, does not have a neutral as there are no components inside that require a neutralSince the rule in question only applies to one and two family dwellings, it extremely unlikely that there would be any panel that does not have a neutral. There are GFCI breakers larger than 50 amps.
But the source panel does.The control panel for the heaters, does not have a neutral as there are no components inside that require a neutral
Are you saying then that a neutral wire needs to be feed to the supplemental (heater control) panel to allow for GFCI breakers to be used in the branch circuits or that the supplemental panel can be protected from the source panel?But the source panel does.
That the GFCI protection can be in the source panel.Are you saying then that a neutral wire needs to be feed to the supplemental (heater control) panel to allow for GFCI breakers to be used in the branch circuits or that the supplemental panel can be protected from the source panel?
Is an A/C condenser an outdoor outlet?That is 100% false. I just spoke to him the other day on this issue.
Is an electrical disconnect an outdoor outlet?That the GFCI protection can be in the source panel.
Your answer would be correct if you replace the word "outlet" with the words "receptacle outlet" everywhere.Is an A/C condenser an outdoor outlet?