Of course it was taken down...his business is selling the books and videos, not giving that stuff away for free.
Yes, the rule in 625 only requires a receptacle that supplies an EV charger to be GFCI protected. However that does not have anything to do with the rule in 210.8(F). If CMP wanted to modify the rule in 210.8(F), they would have to say something like, hardwired EV equipment shall not have GFCI protection. They could do that under the provisions of 90.3, but they have not done that. Saying only that receptacles supplying the EV equipment must have GFCI protection is not even close to saying hardwired EV equipment shall not have GFCI protection.
If you want to change this, you need to submit a PI for such a rule in 625.