Re: 220 HVAC disconnect box clearance
The pullout, disconnect or whatever else it can be called is required, as Don just posted, to have the working clearance per 110.26, there are no exceptions!!! This ruling is here to protect the technician, whether it be an HVAC person or electrician. The lockout does not rule out the disconnect requirement for this piece of equipment, unless it is an industrial location, 440.14 & 440.14 exception #1.
If there is a problem with space, you are permitted to mount the disconnect on the equipment, 440.14.
Pierre