Re: 220 HVAC disconnect box clearance
What if some one used a double pole 30 amp rated switch? It is allowed as a disconnect isn't it?
Would it fall under 110.26?
Just a thought. I know the code does not spell it out. that a switch that has no exposed energized parts would not need the space. But as 110.26 is written it does allow for question's as to what the CPM's were wanting. As they use the term "exposed live parts" a few times in this article and even in the 3 condition's that we are suppose to use to know what the size of the space is to be. And if the equipment does not have any exposed live parts how can you use the condition's.
I'm no English master but to me the intent of 110.26 is to prevent a shock hazard when someone has to open a box that has live parts in it to give adequate room to preform service with out the danger of accidentally touching something live or causing a short circuit that would cause burns. I know the hassle of working on equipment that is put in tight spaces. but if this equipment is not required to be worked on while energized (as what the manufacture requires) then it is nothing but an inconvenience. look at the auto how many times we cursed they way they make it hard to change parts on them. the "71" pinto and maverick both had to lift the engine half out of the car to change the starter. But the manufacture still makes them hard to work on.
I have always been taught that the NEC is for safety not for something that might be hard to work on. I have to go with the interpitation that this disconect does fall under 110.26 until they change the NEC wording of 110.26, But I still dont think all disconects meet the intent of the wording, or we would be requiring this space around all disconects, Receptacles, switch's, Etc...
What if some one used a double pole 30 amp rated switch? It is allowed as a disconnect isn't it?
Would it fall under 110.26?
Just a thought. I know the code does not spell it out. that a switch that has no exposed energized parts would not need the space. But as 110.26 is written it does allow for question's as to what the CPM's were wanting. As they use the term "exposed live parts" a few times in this article and even in the 3 condition's that we are suppose to use to know what the size of the space is to be. And if the equipment does not have any exposed live parts how can you use the condition's.
I'm no English master but to me the intent of 110.26 is to prevent a shock hazard when someone has to open a box that has live parts in it to give adequate room to preform service with out the danger of accidentally touching something live or causing a short circuit that would cause burns. I know the hassle of working on equipment that is put in tight spaces. but if this equipment is not required to be worked on while energized (as what the manufacture requires) then it is nothing but an inconvenience. look at the auto how many times we cursed they way they make it hard to change parts on them. the "71" pinto and maverick both had to lift the engine half out of the car to change the starter. But the manufacture still makes them hard to work on.
I have always been taught that the NEC is for safety not for something that might be hard to work on. I have to go with the interpitation that this disconect does fall under 110.26 until they change the NEC wording of 110.26, But I still dont think all disconects meet the intent of the wording, or we would be requiring this space around all disconects, Receptacles, switch's, Etc...